what is the main purpose of line PT and bus PT?

Answer Posted / nageswara rao

line pt means measure incoming line voltage and protect line
under voltage protection 88% of voltage,bus pt means measure
out going bus voltage and protect bus under voltage
protection for motor feeders,44% with time delay 3-5 sec,
pt means the potential transformer, which is used as a
instrument transformer in measuring device. its main use is
to step down the voltage at measurment levels.

Is This Answer Correct ?    125 Yes 15 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

WHAT ARE THE DATAS REQUIRED FOR PROTECTION AND METERING AND CONTROL AND LOGIC PREPARATION,HOW TO STUDY THE PROTECTION AND METERING?

1687


If not into production, how far did you follow the design and why did not you see it into production?

1708


what is the need of starter in tube light and what type of starter is used in that?

1513


please tell me, how i clear the objective test? when i studied form the one book after i solved the objective ,that time i solved that qes. but if i tried solve objective form the other book then i could not solved these que.

1236


sometime battery charged and then automatically charged when rectifier ON conition, is there any chances please clarify the same.

1375






if in 3-phase system voltage=440V,frequency=60Hz, current=400A. then if it is single phase then current=? and if it is single phasing then current=?

2125


In a single how much maximum current and watts using

1641


Is there any relevant technique to produce power from light and heat energy of the sun simultaneosly from same rays of light?

1409


How to Design green buildings services? What is the advantage to design green building?

1368


how to choose cable size with respect to load? how to convert cable size in mm2 to sq.mm?

4827


What is the formula formula for Busbar sizing and what are the things to be consider for Busbar Calculation?

1987


what is difference between window type and wound type transformers?where we will use window type and wound type transformers?

1724


Advantages/Disadvantages of earthing of neutral bus on MSB instead of separate neutral earthing for transformer/DG sets feeding to MSB

2305


can i connect REF and Differencial relay in 1 CT core for transformer protection?

1463


How to calculate no of EARTH PIT? Describe the formula as per IS standard?

3190