how calculate gd2 of ht motors
Answer Posted / kuldip dadhania
Motor GD2 = (Load Gd2 x Motor RPM x Load RPM)/
(Motor RMP x Motor RPM)
Is This Answer Correct ? | 6 Yes | 5 No |
Post New Answer View All Answers
how to avoid Saturation in C.T?
what is meant by re-rolling motor? how it differs from standard motor?
What is the main use of rotary phase converter ?
I have a situation to design sub-Distribution board/Panel meant for feeding power sockets. In the incomer CAN i Take TP MCCB with Neutral Link and All the outgoing feeders with to sockets with TP MCCB and Neutral Link? P.S : My System is IT Earthing
How is operate breaker failure scheme in substation
what is the purpose of slope in the differential relay?why we are using two slope?but in busbar differential we are using only one slope.why?
How would you calculate power loss in a resistor?
what is the terminal voltage of dc series generator running at rated speed at no load?
how can i use REF and diffrencial relay both in 1 CT core for transformer protection?
Whether should be the oil level in OCTC transfomer? It should be upto winding immersed completely or should be upto tap changer s/w? How it will affect the performance of the transformer. Rating may be 33KVA
What is the basic rule for block diagram reduction technique?
Factory acceptance test. FAT. For 132 kv transmisstion towers what is that meaning and what are the tests commonly companies perform now days.
TRANSFORMERS WITH DC SUPPLY
What is the difference between hot and cold loop testing?
why electron produce magnetic field when it is in motion?