what is the difference between UPS & Inverter
Answer Posted / nareshji
ups means un inturrupted power supply with a strict voltage
regulation and below 8 mili second transfering or switching
capacity of load to battery operated mode it gives perfect
output which is between safe limit of critical costly
precise components like medical instruments or computers
while inverter is low cost version of ups means its output
voltage is not so presisely regulated it may very between
large voltage range and mostly used to run fans and
household tubelights if you will use ups it will
continuously run your computer in case of power failure
while if you use inverter then there is chances to switch
off and restart of your computer and loss of all your
unsaved data
thanks
Is This Answer Correct ? | 13 Yes | 2 No |
Post New Answer View All Answers
What is domestic transformer? Draw the connection of domestic transformer.
Why open circuit test of transformers is conducted at rated voltage??Why not any other voltage??
what r substations?what r there work?why voltages r incresed and then reduced during distribution of power
Is it possible to operate a synchronous 2-poles turbogenerator with a still-in-place faulted bar but electrically disconnected ???? If yes, should I act on the other phases as well ???
What is the technical difference between On delay timer and a Star delta timer?
what are the steps involved in generator load test?
what is the function and use of cable differential protection relay?
If I want to lift the water at a height 50m from ground level through two inch(diameter) metal pipe then what is the capacity of motor pump is required? is it possible in single phase supply or not?
what is the effect of back reactive power on the generator ?
Can we indroduce the principle of single phase induction mator to Transformer? i.e. by Producing rotating flux in the transformer.
What is deference between MCB & MCCB & ISOLATOR
What are the two segments of nyquist contour.
How to calculate capacitor bank value to maintain unity power factor with some suitable example?
i want wipro vlsi placement pattern please send me
what are the preventive maintanance actions taken for air circuit breaker? please answer me