For design purposes we can calculate the required knee
point voltage of a CT as follows.
Vknee= (50/In) + (If/(800/5))*(Rct+0.081)
In = CT secondary current (5A)
If is the fault current expected to flow through the CT
Rct - Resistance of the CT secondary.

Is This Answer Correct ?    16 Yes 3 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

How do i right a ladder diagram that has 1 actuator that performs a full stroke followed by a half stroke

1623


how we select ac fuse rating of an power inverter???

1388


What is industrial plc

1310


How can eliminate noise problem inside temperature controller temp. variation due to contactor chattering problem.

1192


bitumar

1804






what are types of encoder

1431


Why we specify TNC switch with 1NO 1NC ,2NO 2NC ? how we get connection.?

1266


What is the meaning of floating point earthing in battery backed systems ?

1483


please give me all the Alarm .Trip ,Safety Relays & Conditions of UPS Systems mail me on ashokbabunhce@gmail.com

1371


Explain the operation of variable frequency transformer?

672


How many types of probe used in cro?

665


If rotor works in clock wise what happens

1448


how dia of wire and angles are calculated for overhead shielding wire to protect substation equipment from lightening strokes???

1574


sir am giving jspl exam on 19th oct . i belong to eee, so plz send previous question papers ..........to dis id abhilash203@gmail.com

1994


what is a composite error in current transformers, why occurs & in which it will occur i.e, either metering ct/ protection ct

1300