what is the significance of tan delta testing?explain the
theory?
Answer Posted / veena nair
tan delta testing is usally carried out to check the
healthiness of insulation.so this testing is usally carried
out in cb ,ct, bushings etc ,for all these equipements one
standard value will be there,for breakers this value will
be 0.00073, if any devation in this value we have to
suspect about it insulation healthyness.
Is This Answer Correct ? | 22 Yes | 10 No |
Post New Answer View All Answers
Advantages of using generator circuit breaker (GCB) scheme in a power station ?
Draw torque - speed curve and load curve of induction motor? mark operating point ?
in HT service 3ph 4 wire service Y-phase voltage shows zero . whether it is meter fault? or what be the reason ? if y-ph voltage zero ,can current is recorded? reasons for failure?
what is the relation between reactive power and power factor for the what is the limit of reactive power and power factor
what is the use of sdf?
How to see the inductance in a transmission lines
how is the incoming cable size calculated for a given current rating of a panel??
How can we calculate the KVA rating of a Distribution transformer from its core details?
diameter of cable and core is doubled then the value of capacitance is
How many Zones can be in Conventional type fire alarm system & how can we detect the fire in Conv. type FAS?
Can you explain about TEE protection scheme?
Why does the adjacent zone of protection overlap?
. What is Electrical Life & Mechanical Life of Circuit Breaker? 2. What is Electrial Life & Mechanical Life of Magnetic Contactor? 3. What is RCD, RCCB & RCBO? 4. What is the Between defferance of RCD, RCCB & RCBO?
When can we take Neutral as common neutral link?
What is the difference between shortcircuit current, rated current of cable & MCB with example? What will be the size of cable required for 5.5 KW motor (Full load current 10 Amps approx.), Starting current with DOL is 120 Amps. Aprrox. Short circuit current with LLLG fault is 2000 Amps Approx.