What is vector group? What is meant by DYN11?Why is it needed?

Answer Posted / sukhdev negi

Abobe two reply explained correctly "what is vector group".
The answer to the last question "why it is needed" is as
follows:-
By virtue of constrction & terminal connections of the
transformer, a phase difference between primary vector &
secondery vector occurs. We need to know the same for the
following reasons:-

1)Matching of vector group is required (to avoid
circulating current/ fault ), when 2 transformer need to be
operate parallal on a common bus/system.

2) to provide transformer differential protection correctly.

Is This Answer Correct ?    16 Yes 11 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

how is working bearing heater?

1559


why transformer ratings in kva? & DG ratings in kva? & Motor ratings in kw/HP?

1112


Two bulbs of 100w and 40w respectively connected in series across a 230v supply which bulb will glow bright and why?

622


what are the dimensions for 200 kva transformer plinth (plateform),in which pcc m20 is used..

10774


i want wipro vlsi placement pattern please send me

1307






How to Calculate The sag of OPGW in Transmission Line???

2663


Why reactive power is needed in a power system? How is it being absorbed or delivered by alternators? For reactive power control we are changing excitation but reactive power absorbing or delivering related to stator. How these two are interlinked? i want a detailed explanation with necessary expressions and figures?

1401


Define super node?

726


what is the preventive maintence for ht panels and busbars and vcb abd acb's.

1862


What will be the output voltage of a transformer if it is primarily energized from a square wave voltage source?

678


What happen if we apply square wave or traiangular waveform voltage to the transformer primary winding instead of sinusoidal wave?

1638


We have a couple of oil tanks at our plant. One of them does not have a lightning arrester installed. My question is it necessary to install an arrestor on every tank or will this particular one be covered by the arrestor installed on the ajdacent tank, Since all the tanks are close to each other. Basically, I want to know that if these arrestors or protection works in a parituclar area of effect or influence. Thanks

1555


What is earth system using on the floater TN-S or TT. Iam not sure and what ICCP

1243


oltc of a transformer, how it works? and what are the equipment consist of describe briefly?

1568


Describe Non I.S. Earth System and why is it used?

1292