how to calculate the kw, Amps consumed by a capacitor,
give me the formula for KVAr into capacitance,KVAr into KW
& KVA, Amps

Answer Posted / bijan

(KVA)2 = (KW)2+(KVAR)2

Is This Answer Correct ?    3 Yes 5 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What is the difference in calculating size of AC cables compared to calculating size of DC Cables? Usually DC Cables are larger than AC Cables although they have the same ampacity. Why is it?

1527


What is time invariant system?

692


what is lumped and distributed elements?

1552


from generating station If 400v LT line length is 1000m how much voltage is drop and how do i calculate it? which cable will be use for this line?

1541


What are the three major categories of error?

675






What is the function of electron gun used in crt?

603


How one may guess the direction from which the distribution line is incoming if there is no pole plate on poles?

1678


what is KA rating and how can we choose switchgears on applications

972


Is a contactor (or master relay) required between incoming lines and a VFD? The question goes to safety. If a contactor were used before the VFD and an e-stop engaged then the motor will coast to a stop (i.e. VFD loses power) instead of stopping much faster if the VFD braking fucntion were used. It would make more sense to keep power on the VFD.

1563


WHY DO VOLTAGE TRANSFORMERS FAIL DURING EARTH FAULT IN THE DELTA CONNECTED 6.6KV ELECTRICAL SYSTEM

1550


what is the IEC standard for Power Cable installation in onshore (like in direct buried ground or above groung)

2139


What is VCB? where it is installed at SP. What is SP?

1743


block diagram of 2 ups system connected in hot stand by mode?

7495


physical identification of HT & LT panel

1213


Direction of flow of active power and reactive power with logic?

1316