what is the difference between squirrel cage & slip ring
induction motor?
Answer Posted / thowsif_emerson_csm team
The windings on the rotor of a squirrel cage motor is
comprised of aluminum (or sometimes copper) bars embedded
in the steel laminations of the rotor. The ends of the
rotor bars are shorted together by rings at each end of the
rotor. There is no external electrical connection to the
rotor. The bar and ring structure looks like an exercise
wheel for a pet squirrel.
The rotor of a slip-ring motor is wound with wire coils.
The ends of the windings are connected to slip rings so
that resistors or other circuitry can be inserted in series
with the rotor coils through carbon brushes that slide on
the slip-rings allowing an electrical connection with the
rotating coils.
| Is This Answer Correct ? | 230 Yes | 21 No |
Post New Answer View All Answers
Whether power factor should be high or low? Why?
I'm looking for a mnaual set for a Teradyne J750. Softcopy would be preferred but I'll take what I can get.
In case of generator when we consume more power produces by it why load on generator increase and starts sound more. and how it is adjusted..
How test for Ddo vector group test condition?
What is the difference between shortcircuit current, rated current of cable & MCB with example? What will be the size of cable required for 5.5 KW motor (Full load current 10 Amps approx.), Starting current with DOL is 120 Amps. Aprrox. Short circuit current with LLLG fault is 2000 Amps Approx.
Name the component u would expect to find in a switchgear assembly?
What is frantic effect?
In how we connect watt meter for open & short circuit test of a single phase transformer.
What is ignition module of a CAT Gas Genset G-3508 Engine, Alternator SR4B Series. HOw its checked for correct functioning.Is it repiarable or replacable?
What will happen if the voltage in my house drops from 220V to any lower voltage?
how i calculate the syncrones generator NGR resistance .if we have a 6mw generator line voltage of generator 11kv also line current 393.3 ampere.
Pls explan the OLR setting in VCB at HT yard
How to calculate the phase to phase clearness of HT /// LT bus bar?????
what is the voltage between earth to neutral in lift.
Is it advantages of having star-delta vfd than normal star vfd , if yes why?