We have 3 Gensets 1.500kva,2.380kva,3.250kva How can we
connect in common busbar&we have variable load.
Answer Posted / vishvesh
yes, we can connect this three generators in one busbar,
after fulflling following conditions.
1.voltage should be same.
2.frequency should be same.
3.phase sequence should be same.
after shynchronizing of all three outputs, we can
connect it to the common busbas.
Is This Answer Correct ? | 12 Yes | 0 No |
Post New Answer View All Answers
will 1050kva DG set withstand for back charge of 16MVA transformer
what is the meaning of WYE and DELTA in Electric meter?
direction of tarbine& genrator
1.why we are using metal oxide gapless block in lightning arrester,2.What is minimum and maximum rating of metal oxide blocks using in india
2- What are the percentages between excitation currents in phase (R, S and T) in ∆ and Ỵ connections in excitation Current test in transformers?
What are safety device in vcb and acb?
What is the operating principle of turbo-generator.
how to caculate cable size for diff types of loads? if anyone know the calculating procedure please tell me
i want to know how to determine that a surge arrester work properly in 11kv system. and how to test a 12kv surge arrester
What kind of maintenance is conducted for Transformer
How to calculate the no of Ceiling fan (1200mm sweep) per unit area?
What is the main cause of magnetism?
How much load can be taken for chiller from 1500 kva transformer
Why using synchronising methed in DG's sets?
How do the synchronizing lamps indicate the correctness of phase sequence between existing and incoming alternators?