Answer Posted / sumit salunke
Theory
From Ohms law, the voltage drop in an electrical conductor
is
V = I R
where
I = Current, amps
R = Resistance, Ohms
The electrical resistance can be derived from the
properties of the conductor material.
R = ρ L / A
where
ρ = Resistivity, Ω mm2 /m
L = Length, m
A = Cross sectional area, mm2
Watch the units in the above equation.
The resistance can also be expressed in terms of the
material conductivity (ψ) which is just the reciprocal of
the resistivity.
R = L / (ψ A)
Table 1. Typical material electrical conductivity
Material Conductivity, ψ
Copper 58
Aluminium 36
Mild Steel 7.7
Combining Ohms law with the resistance expression, we get.
V = (I L) / (ψ A)
Now, we can define an acceptable voltage drop in a
conductor. I have calculated the voltage drop that was
used in several published tables and get around 5.5 Volts.
We could therefore re-arrange this equation to give the
cable size. But cables come in standard sizes measured in
mm2. In addition, you also need to consider the maximum
current for each cable size.
Table 2. Conductor sizes and maximum currents
Cable Size, mm2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150
185 240 300
Maximum current, A 13 21 28 36 46 61 81 99 125 160 195 220
250 285 340 395
Is This Answer Correct ? | 3 Yes | 0 No |
Post New Answer View All Answers
what is solkor relay and which condition it will act?
why power not passes in plastic and rubber material
What is the difference between voltages or potential difference? And what are they?
What is the function of a neutral reactor.
what is Fault level? why it is calculated? how will u decide same for our plant?
what are the different sizes of U.G. cable & where these cabl;es are used according to voltage ..
When distance between two pulleys is not fixed, the tension of belt is adjusted by a) driver shaft b) driven shaft c) adjustment screw d) belt
what is the setting of locked rotor in HT motor ? (answer expecting in percentage)
In india, according to trade theory above 5 HP motor reqired star delta starter. But we R connect 11 KV motor with 14MW in Direct to line ( With VCB starter combination) Can U Guess, How it is possible ?????
What is the difference between Droop vs Isoch Control?
How many types are using in 220kv/400 kv swith yard
What is the difference between resistance grounding system and resistance earthing system?
sir i want previous entrance exam papers for written test
why we can use 1 to 5V dc
Shall I use 40A semiconductor Fuses in 32 A SFU ? Frame size is same. What Happen if Fuses burn on SFU?