what is the working difference b/w softstarter and
Variable frequency drive ?
Answer Posted / kk_london
in soft starter you cannot control the speed of motor where
as in vfd drives speed can be varied by giving digital
inputs to the drive via plc. But both can control the
starting torque of the load.
| Is This Answer Correct ? | 6 Yes | 1 No |
Post New Answer View All Answers
How can we measure earthing resistance test (Earth meggar) of Transformer neutral pit while in live condition?.
How select ELCB for 32amp. socket having quantity 12Nos. We have to do this wiring in PLANT. Please Also explain the incoming cable specification.
how we can do the insulation on secondary of ct explain and so that tan delta will within limit
How to calculate impedance volt in Transformer?
what purpose to use excaiter in DG.?
why chock were used in old tubelights but are not newest tubelights?
Why we find the sensitivity for the CT's to check?
what is meant by the phrase 'static load' in case of shorting in a generator excitation system?
Comment on the working principle of operation of a single-phase transformer.
what is the prinsiple of dc motor and construction and working ,application of dc motor.
A 2083kva AVR was tested, phase to ground shows continuity, what is the implications
in dc shunt motor if field winding is shorted then
Explain advantages of storage batteries
Define characteristics impedance?
why we are using earth pit in sub stations.?