single phase motor can't self started so we use another winding only in starting and then this winding disconnected due to motor speed and also connect a capacitor to make phase different to generate rotating magnetic field but in 3 ph this not happened because rotating magnetic field is self generated due to phases different angle which shifted by 120 degree
Is This Answer Correct ? | 18 Yes | 6 No |
Post New Answer View All Answers
Is the installation of the filter cloths necessary before spreading the gravels at the transformer yards?
What is the theoretical reason for the size of a zig zag grounding transformer to be 1.732 times less than that of a wye-delta grounding transformer used for the same application?
Vibromotor 252MV 1/4HP2P..what is mean by 252MV?
what is power factor ? how we can calculate the low power factor and amount of capacitor for improve that low factor ?
Why frequency changes due to load variation in power system ? i.e why when load increases frequency decreases?
A 100KVA SINGLE PHASE TRANSFORMER 10000/200V,50HZ REQUIRES 300V AT HV SIDE TO CIRCULATE FULL LOAD CURRENT WITH LV SHORT CIRCUITED.THE INTAKE IS 1000W.THE % OF REGULATION ON FULL LOAD AT 0.8 PF LAGGING WILL BE HOW MUCH AND THE SECONDARY TERMINAL VOLTAGE ON 0.8 PF LEADING WILL BE
Draw the line diagram of diffretial relay connected to transformer?
what is high and low cut off voltage of BB and DG at SPS????????
how to setting Load amps tripping time and extra settings for load Transformer protection relay with RMU panel using C&S model relay..?
What is the effect of atmospheric pressure & Temp; on efficiency of motor? Why NGR(Neutral Grounding Resistor) is used in 132/11 KV Transformer & how? What is the use of Auto T/F in Grid Station?
In single phase capacitor motor, if the motor rotate reverse direction then how much power will be consumed by the motor and why?
explanation of mesh bus bars
What is Tachometer used to measure?
What is the safety of UPS?
Explain about how is it working Earth fault'relay and wahts the resistance value of earth bed