what type of protection and safety req. in the 220kv
substaion and area around the substation

Answer Posted / atul pradhan

Protection:-
1)Distance prot. relay
2)local breaker back up LBB relay
3)differential prot. relay
4)pole discripency relay
5)trip ckt supervision of sf6 gas relay
6)air pressure monitoring relay

Safety precautions:-
1)remove all vegetation inside yard
2)proper earhing to fencing & gate
3)proper watering & checking of earth pits
4)periodical cleaning of all C.T.,P.T.,etc insulators
5)while opening or closing off load isolators always wears
H.T. gloves
6)while closing isolator ensure that all 3 poles fixed
properly
7)monitoring the leakage current of lightening arrestors

Is This Answer Correct ?    9 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

How to calculate mf when meter equipment and meter are connected

1275


How to do stting of vl250 siemens MCCB

2490


Is better to supply the voltage for static exciter from the auxiliary power source or from the SG terminals? And why?

1493


As per standard, transformer body earthing and other Equipment earthing (Equipment earthing) did not connect. but in LT side termination we are doing metal glanding in both side Transformer to PCC Panel through armoured cable, now X'mer body earthing and PCC Pane earthing (Equipment earthing) both are connect.is this safe for X'mer or other equipment?

1201


being an electrical engineer why you wanna come into software i have an very good academics what answer i have to give

1486






which IS or IEC is used for earthing,breakdown voltage of transformer oil, hv/pd testing and all type of electrical testing

2216


Why is remote backup preferred to local backup?

1498


what is allowed value of zero sequence impedancce of 6.6 kv nuetral earthing transformer ?what is the actual value

1661


Dear sir my name Ankit i m Diploma holder present working in Welspun Corp ltd Anjar as Asst.engg (salary 14400/month ctc) i Would like to change my company also i have selected in ford India pvt ltd Sanand as trainee Tech with salary 12000/month so please suggest me for changing my job hope for *ve response

2430


What is the one main difference between ups & inverter ? And electrical engineering & electronics engineering ?

666


please explain to me how to calculate current,voltage,resistance with formula??

982


please give me all the Alarm .Trip ,Safety Relays & Conditions of Chiller mail me on ashokbabunhce@gmail.com

1362


how synchronous condenser is used in place of synchronous generator with out negotiating IEEE standards? Can i use 3 generators as synchronous generators and 2 generators as a synchronous condensers in an IEEE 14 bus system with out disturbing the standards?

1642


hai iam arunkumar. i have applied for an section enginner in rrb. i want lat 5 years solved question papers. if u have please sedn it to arun30682@gmail.com

1316


how does a submersible pump work..?

1414