How to calculate the current rating of power cables ?
Answer Posted / rachuri_sree
You need to know the distace between source of supply and
the load. consider a voltagedrop of 5%. i.e. 5V for a 440v
system. use the formula V=IR from this you will know the
resistance required for your requirement. (I is the load
that you want to connect). Use R=Pl/a to find the correct
cross section of the cable. (P is resistivity of either
copper or Aluminium, l is the distance).
Is This Answer Correct ? | 12 Yes | 7 No |
Post New Answer View All Answers
how we decide wire gauge for ac or dc coil and what is the basic diff. B/w these two coil?
What is meant by system?
Can anybody post questions asked in Engineers India Limited Interview? Thanks in advance.
When a single pase capacitor run motor- run on 230vac and Case(1)run with 8 Mfd 250 vac.capacitor , Case( 2) run with 8 Mfd 400vac capacitor. What is difference between both case regarding power ,efficiency etc?
Whar is the KvA rating of 33Kv substation & actual kv rating of power generaating station.
What is the formulae of Megger value for a A.C.Motor
what is the difference between general inverter and solor inverter clerly explain plz
explain working principle of earth leakage relay
what is mean by Digital Logic Meter (DLM)
how to calculate magnetic force genrated by a coil ?
When semiconductor fuse does save thyristor in each cycle of conduction? Why under voltage setting keep less in SPRS and more in DC drive?
WHY SEPARATELY EXCITED MACHINE NEEDS EXCITATION BY DC SUPPLY WHY NOT BY AC
how to calculate units consumption for a 12 hp motor /hr.
how to design step down 12 V, 1mA small transformer from 220 V AC? Because according to VI relation and power transfer it results bulky...
how to select the isolation tranformer for siemens 802dsl cnotroller