which %age if losses increases when frequency is increased
to 25%
Answer Posted / ramesh kumar k
Rahul & Balaji both are right...
As the HYSTERISIS and EDDYCURRENT Losses are directly
proportional to the Frequency, definitely they will increase
and also the reactance also increases with increase in
frequency the reactance drops are also increased...
Is This Answer Correct ? | 3 Yes | 0 No |
Post New Answer View All Answers
Why it is necessary to isolate fire fighting when you are taking shutdown for lv board.
Why the moulded plug comes with domestic appliances instead of assembled plug like anchor, Vinay 5/15 A.
difference between high and low impedance BUS BAR relay??
Can i use the B-curve MCB instead of C-curve MCB
Explain the propagation of harmonics in the network and influence of phase angle of harmonics.
Differenciate between circuit wiring and sub main wiring with illustrations
ho can we calculate the conductor insulation value according to their ratings like voltage,current etc.how insulation value related with voltage,current and power of amachine
The power supplied to a 33microF capacitor from a 120V, 60Hz source will be
what is upper impedance and lower impedance of a distance relay
1.why should we connect the measuring instruments in l.v side in short circuit test of a transformer? 2.why the power factor is less in open circuit test of a transformer?
As a electrical engineer.. what are the basic norms should follow in transformer oil testing.. 1.What is the Electrode type? 2.How long time you will give for oil testing?
is that a problem if i connect a single phase load to a secondry delta connected transformer but i get a neutral from other transformer i the system?
Starting Time of LT & HT Motor
Is it possible to make a 5P10/ CT Ratio 50/1A Burden 5VA
what is the carona effects meaning in HT line transmmission system