Please tell me 1 ton = How many Kilowatt (Electrical)
Answer Posted / avnish sharma
1 ton = 12000 BTU/hr
and to convert BTU/hr to horsepower,
12,000 * 0.0003929 = 4.715 hp
therefore 1 ton = 4.715*.746 = 3.5 KW
| Is This Answer Correct ? | 83 Yes | 50 No |
Post New Answer View All Answers
Define Electrical Insulation and examples of Solid,Liquid and Gaseous insulating materials?
how to select proper cable for ct wiring so that drop within the limit.
how to find Harmonics and types as per the equipemnts
what should be the ideal gauge of wire (In sq mm) for different loads in Ampere?
What is signal flow graph?
Is a contactor (or master relay) required between incoming lines and a VFD? The question goes to safety. If a contactor were used before the VFD and an e-stop engaged then the motor will coast to a stop (i.e. VFD loses power) instead of stopping much faster if the VFD braking fucntion were used. It would make more sense to keep power on the VFD.
which phase is preferred for connecting 1 phase vt used for synchronizing OHL? WHY?
RESPECCTED SIR/MADAM- I AM PRERING FOR SECTION ENGINEER (ELECTRICAL) RRB CHANDIGARH PLEASE SEND ME SOME PREVIOUS YEAR QUESTION PAPER OR MODEL PAPER.MY EXAM IS ON (30- NOVEMBER 2008).I AM VERY THANKFUL TO YOU. FROM- HARENDRA SINGH YADAV
What is the difference between Generator Differential Relay and Transformer Differential Relay?
Which Class insulation is prefered for the sandwich Busducts ? Why?
why the India electrical supply transmission loss is high when compare to us
what is mean by restructuring power system?
What is the capacitance values of 132,220,400 & 765 kV current transformer
1. What is the exact formula for one weber? for example,(one ampere = one coulomb electron of electrons crossing a point of conductor at one second. i.e, 1A=1Q/1sec)
xfhnchncv?