star delta connection used in reduce the starting current
at 3 times . how its reduce the current please explian .
Answer Posted / m.varadarajan
when higher hp motor starts with high current, to reduce
the starting current we are using this connection,it will
reduce 1/root3 times of full load current, after motor
reaches of the rated speed, delta connection applied.this
time full voltage applied to winding and motor run smoothly.
Is This Answer Correct ? | 17 Yes | 23 No |
Post New Answer View All Answers
what is relay what is protection & contact multiplying relays where it is used function in brief
What will happend if given Vfd out put to step up transformer
how meger function
what is the working principle of a DG Set, Alternator, & exiter
how braking & making capacity of circuit breaker is calculated?
HI....HOW CAN BE MESARED THE VALVE OF NEUTRAL GROUND RESISTOR WHIC IS LOCATED AT SWICHGEAR ON GENERATOR SIDE....
What is referred to the electron in the outer orbit?
What it the purpose of parallel phasing transfomers??
in power generator normaly voltagr betwween esth to neutral is 0 but my work place generator show the volatge is 60v any body know why? thanks
What is pi controller?
1)what is the function of a frequency inverter? 2)If a few frequency inverter are connected onto a device network,what are the two setting that will ensure the frequency inverter work properly on the network. 3)whats is the name of the input sensor for weigher? 4)How to confirm that the load cellis faulty? 5)Describe briefly the steps to validate that the weigher is working properly? 6)Describe the procedure to validate the flowmeter accuracy? 7)Describe briefly the steps to validate that the tempreture sensor/transformer is working properly. 8)what is the adjustment that need to be done when you are calibrating the temperature transmitter ? 9)what are the safety measures to be taken before disconnecting motor for rewinding. 10)whats is the synchronous speed in rpm of typical 4pole 50hz motor? 11)whats is the formula for kw, ohm's law 12)if a 3phase motor is rated 3kw,415vac,what is it's rated ampere?
what is smartµ grid technology?under coal gassification?
What is a differential amplifier?
In which working principal temperature transmitter work.explain in detailed.
how can you calculate fault level ?