How to check the specific gravity of the two 12 V batteries
connected in series to a 24 V UPS and inverter ?
will we have to disconnect all the connections and turn off
the UPS and inverter or not ?
will we have to check specific gravities in each cell of
the two batteries ?
what is the name of the instrument that is used to check
the specific gravity and whats the procedure to check the
specific gravity with it ?
thanks
Answer Posted / hemant nimbalkar
There is no need to turn off the ups or remove the
connection.We can check spec. gravity at the time of
battery charging.Spec.gravity is checked by hydrometer.Just
immersed the the hydrometer in each cell which have to
mesure.Press the rubber handle &take some electrolyte and
mesure sp. gravity. the value should be 1200-1250.
| Is This Answer Correct ? | 10 Yes | 1 No |
Post New Answer View All Answers
A ray hit a smooth regular surface at an angle of 20 from the normal. Calculate : 1. The angle btw the incident and reflection ray. 2. The angle of deviation.
what is the circulate the diesel in DG in side pls tell parts name and picture with circulate the diesel
What is stacking factor? What is its approximate value?
What is the procedure/activities to be taken to inject the current more than 2000A by using 2000A Loading Transformer?
Can you used moeller lzm1 mccb in a dc system with 125vdc and 20ka short circuit current , beside is it have 24 or 48 volt shunt ? Beside how long current can through from An MCB shunt contacts? (like Z7-AS 24 V)?
why we are not giving the zone 1 trip command to the master trip relay
please tell me how a surge protector work on a DC 48Volt.? please describe briefly.
How is the gain affected by the introduction of feedback in a control system.
How you will determine the volume of oil in a particular Distribution transformer.
What range of speed can you get with the field control method of speed control of d.c. Shunt motor?
how to set relay setting? and example calculation...
Why dry type cast resin transformers tap link blast in HV side while power shut down times on load?
I need model question papers for RRB section engineer Chennai... Please send to my E-mail Id:- maitheerainbow@gmail.com
how to calculate the battery AH
What are dependent sources?