How to calculated capacitor rating both HT
Answer Posted / stanley electrician
capacitance of the capacitor is mentioned in KVAR.
Formula : KVAR = KW*tan@
FOR tan@, First note the power factor & KW without
connecting capacitor.
The noted power factor is in cos@.Convert the cos@ value in
tan@.
for ex. If power factor is 0.6, KW = 200
cos@ = 0.6
cos-1 (0.6) = 53.1
tan (53.1) = 1.333
200*1.333 = 266.6 KVAR
if you use 266 KVAR capacitor, Then the power factor
improves to unity (1.000).
Is This Answer Correct ? | 20 Yes | 12 No |
Post New Answer View All Answers
what is the step by step formula for calculating bus bar phase and neutral size of a panel board.suppose the incomer of panel board is 100A..???step by step answer please
What do you mean by dependent and independent voltage sources?
Show Details FROM:Muhammed Ikram TO:qa@allinterview.com Message flagged Saturday, June 4, 2011 10:07 PMMessage bodyHello all, i want to ask a question to all of you that what is VMM (voltage monitoring module )? how it work,s? i heard somewhere that it compare 1 phase voltage to other phase voltage. but there is also some setting on it. how to set it,s setting. please tell me briefly. Thank,s and Regard,s. Muhammed Ikram.
Give some differences between open loop and closed loop?
How to do maintenance of transformer feeder.
all interview questions with answers of ntpc (2000-2009
How can I calculate ISF of current transformer?
Why do we need interlocking in a HT metering or Ring main unit switchgear?
for what purpose the star point is done in ct
a starter used for squirrel cage induction motor?
take 100kva DTR( delta/wye ), what ll happen if we connect 11kv to LT side instead of connecting to HT side? will the DTR behave as a step up transformer or something else????
What is the test block protection relay if any body know plz explained
Draw a block diagramof Three UPS systems connected in Parallel mode?
I have iti elec, 1st aid, and 5 yrs experience in 7.5 mw power plant. Am i eligeble for 11kv license in telangana state..when, how to apply for that.?
WHY CBCT USE ONLY IN Y PHASE NOT OTHER PHASES