How to connect frequency meter in metering circuit?(single
phase and three phase frequency meter)phase to phase or
phase to neutral
Answer Posted / abdul nazir
Same as volt meter connection.
connected parallel with Phase & neutral.
| Is This Answer Correct ? | 38 Yes | 3 No |
Post New Answer View All Answers
HOW TO CALCULATE CAPACITOR BANK OR HARMONIC FILTER CALCULATION
What is the effect of solar radiation on the design of an Isolated Phase Busduct?
what is v/f control in VFD?
How line capacitance & line inductance varies with increase in height tower.
Why we do 2 types of earthing on transformer (ie:)body earthing & neutral earthing , what is function. I am going to install a oo kva transformer & 380 kva dg set what should the earthing value?
What are the application of filter?
What will happen if the voltage in my house drops from 220V to any lower voltage?
what is the chemical name and formula of refrigarent R-134a.
Dear friends I want to design busbar for1600 kva transformer(i.e2100 amps) what are all the factors to be considered before selectinga busbar what are all the standard sizes of busbars what is the formula for finding current of copper and aluminium busbar
What is the maximum percentage voltage drop (vd%)for a motor control center
which motor have relatively high power factor and what is reason for have high pf? 1.capacitor run motor 2.shaded pole motor 3.capacitor start motor 4.split phase motor
pls tell me about ups internal connection & we have given only 3 phase supply to ups system how get 4 wire (R Y B N )
Define active and passive network?
What is the voltage gain or transfer function of amplifier?
HOW TO CALCULATE THE VT SIZING?