What type of tranformer generaly at soft wares like
capacity 2000 kva 1800 kva etc iam confused it CT or PT
OR distribution tranformer
Answer Posted / pawan dahiya
CT is current transformer and used in high current
PT is Potential Transformer and used in high voltage
| Is This Answer Correct ? | 0 Yes | 3 No |
Post New Answer View All Answers
what topics we have to concentrate for power grid et.written test.and tell what to read for english synonyms and antonyms.
I have motor 1500 HP and , 4160 V , 60 HZ , then i need the rating of transformer which can feed that motor ??
how can i determine the gear ratio for a rack and pinion system if an electronic gate operated by an electric motor is to travel a distance of 5meters in 15 seconds.
what is the cause of voltage dipp or swell in the transmission lines?
how the works electronic energy meter?
What is the difference between electronic regulator and ordinary electrical rheostat regulator for fans?
what is the defination of Cable database? What are the points are considered while preparing cable database? Is there any sample available for cable database?
at work i have a genertor/alternater what is the easyest way to work out if it is dc or ac?
A 100 kVA , 400 v/250 kv testing transformer has 8% leakage reactance and resistance on 100 KVA base . A cable has to be tested at 500 kv using the above transformer as a resonant transformer at 50 hz . if the charging current of the cable at 500 kv is 0.4 A find the series inductance required . Assume 2% resistance for the inductor to be used and the connecting leads . Neglect dielectric loss of hte cable . what will be the input voltage to the transformer ?
A cylindrical wire is compressed in length by 10%. The percentage decrease in the resistance will be?????
Match the following a)(X'+Y') b)X'Y' C)XY 1)NAND 2)NOR 3)Carry
What do you mean by ratio correction factor of instrument transformer?
Can anyone please provide me details of MCCB/Contactor/SFU rating calculations for a motor feeder..for example 50 kw.. not from type-2 cordination chart. i want manual calculations..
What difference between ref protection and differential protection ?
Explain the propagation of harmonics in the network and influence of phase angle of harmonics.