how to calculate the current if i know power in MW and
voltage 11kv/415v and also want to know that incoming
cables for trnsformer
Answer Posted / sripellirajukumar
hi this is rajkumar...
as per my knowledge
the primary side current can be calculate as follows
for example
we have power transformer of 5MW transformer and the 33\11kv
the primary current is (5000kv/33kv)/1.732=87.47amps
the secondary current is (5000kv/11kv)/1.732=262.43amps
here 1.732 is square root of 3....
Is This Answer Correct ? | 43 Yes | 18 No |
Post New Answer View All Answers
explain remenance . differentiate high remenance type ct & low remenance type ct
if grounding is notdone at regular intervals for long distance transmission, will the load connected at distribution end receive voltage during negativehalf cycle of the sine wave?
What conditions are required for transformer to operate at low frequencies ?
In siemens S7-300 PLC, what is function and function block ? What is the difference between them ? When to use function and when to use function block ?
What is the function of under voltage release ?
How to Decide(calculate) Bush bar size for copper and aluminiam ?
Witch do depand of Power factor and theory of power factor?
How to calculate loses in transformer of 160 KVA ?
what happen if the supply is given to the stator of the 3phase induction motor with out assembling the rotor ?
How is magnetic leakage reduced?
Can anyone explain me about the capacitor calculation
What should be the amps for a MV fuses for transformer 630kVA 20(10)/0.4 kV
Explain the operation principle, advantages and disadvantages of the following converters: a) A 12 pulse converter b) A Switch-mode inverter c) A thyristor inverter
What is Auto Mains Failure Panel & Auto Synchronizing Panel
What will be electrical cost per sqft for IT building (basebuild and fitout)and for residential township?