How to calculate kva? what is the formula.
Answer Posted / sudheer
KW = KVA X p.f
KVA= KW/ P.F
P.F= kw/KVA
KVAR= KVA.Sin theta
Is This Answer Correct ? | 73 Yes | 14 No |
Post New Answer View All Answers
how can tell us the AC indoor or outdoor which Tr and formulls
is that a problem if i connect a single phase load to a secondry delta connected transformer but i get a neutral from other transformer i the system?
How to measure power in 2 or 4 or n phase circuit? Please give me a formula.
How can we calculate the motor frame sizes?
I want to calculate how much capacitor we connect to maintain the unity power factor? Is there any formula? Pls give me the answer
If the Brush of DC motor is shifted by 90 deg, then what happens to voltage and torque? Both voltage and torque are zero. how to justify the answer?
why do you add the load short circuit impedance when considering short circuit amperage. It seems that you should only consider supply. If you need to consider loads and you don't know what loads are to be added , what would be a good sub-transient reactance rating for the loads?
Why we use mho Relay in long transmission line?
If one lamp connects between two phases it will glow or not?
What is pd controller?
help me with the question that might be ask on the interview for technical position
r we are using in gas turbine mark (5) frame (6) (made in india Bhel 1997) Ā
What is the difference between PS & metering CT (5p20,0.5 etc.)? Why in PS class CT only Vk is given ? Is PS class CT is more accurate than metering CT?
Is RTCC panel needs any control supply.
What is domestic transformer? Draw the connection of domestic transformer.