How do we check transformer losses and what are the ways to
minimise it.
Answer Posted / guest
transformer losses can be found by doing open circuit test
and short circuit test
open circuit test gives the core losses
short circuit test gives the copper losses
note in open circuit test the lv side is given supply and
in short circuit test the hv side is given supply
the iron losses can be reduced by providing laminations of
thinner dimension and using c.r.g.o sheet for laminations
the copper losses depend on the winding resistance which
increases due to heat can be reduced by providing
sufficient cooling to the winding.
Is This Answer Correct ? | 36 Yes | 2 No |
Post New Answer View All Answers
The 3 phase 400 hp 440 volt slip ring induction motor do not take one phase amps why ? The motor is running good condition
how to produsing geretor power
why electron produce magnetic field when it is in motion?
who invented active elements? plz give me the complte details of active elements...
What does the term supermesh means?
what is meant by neutral compensation factor and where it is used
What is a parabolic signal?
how does the thyistor work in dc drive?
Write a note on Treatment for electric shock.
ho can we calculate the conductor insulation value according to their ratings like voltage,current etc.how insulation value related with voltage,current and power of amachine
which stabilizer is better ? AVR, Servo Stabilizer, Static stabilizer etc & why explain it
which is the best institute for PLC,SCADA,DCS in hyderabad
How to synchoronize the generator (with gcb,GT) to grid????? ????? from Grid iam getting power (rated 400kv/20kv) through GT and its goes to UAT.,,ST.,, now my generator(rated 20kv ) ready.,, now iam closing my GCB.,, in GT iam suddenly giving 20kv on that Gt.,, what will happend
What is domestic transformer? Draw the connection of domestic transformer.
What is the basis for selecting Vk/2 or Vk/4 for REF and Differential protection of Transformer and What is the significance of magnetising current