actually at the time of transformer rating decided the
following factor to be consider
1.Connected Load
2.Power fACTOR
3.fUTURE eXPANSION

KW=KVA*P.f
630=KVA * 0.8
KVA = 630/0.8
KVA = 787.5 KVA

So the Transformer size is 800KVA

THIS CALCULATION IS EXACTLY CORRECT

BUT FOR FUTURE EXPANTION WE CONSIDER 30 % MARGINE FOR THAT

Is This Answer Correct ?    80 Yes 13 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

at work i have a genertor/alternater what is the easyest way to work out if it is dc or ac?

1387


How we can calculate the consumption in kwh of motor on basis of kw @100% load, @50% load & @ no load.

2329


What tests should i carry over on a newly rewinded DC Generator with voltage rating of 38 volts and current rating of 350 amps, to certify that the machine is OK?

1429


operation of diesel generator

1544


how to commissioning the genset with amf panel?

1901






What is meant by Low Resistance Cable and High Resistance Cable.

1431


Can u tell me design of switch yard

1693


Some times to change of DOR of a motor, interchange of R & B is not effected and RYB take same current, but interchange of R&Y is effected ie change the DOR. My doubt is what is the problem in motor and how it is happen.

1543


How you give clearance to a spare feeder.

1220


how to calculate the loss tangent of electrical cables

1607


WHAT IS DEGREE OF COMPOUNDING IN D.C MACHINE MEANS? HOW TO READ THE OPERATING CHART FOR ANY ELECTRICAL MACHINES?

4274


WHAT IS THE DIFFERENE IN ACTION OF MCB,MCCB,RCCB

1957


A 2083kva AVR was tested, phase to ground shows continuity, what is the implications

516


when measure the core loss of three phase distribution transformer or three phase reactor loss, one phase shown negative watt loss. why??

1522


What is voltage ratio of a transformer?

637