how we can calculate the transformer size.
Answer Posted / sachin
actually at the time of transformer rating decided the
following factor to be consider
1.Connected Load
2.Power fACTOR
3.fUTURE eXPANSION
KW=KVA*P.f
630=KVA * 0.8
KVA = 630/0.8
KVA = 787.5 KVA
So the Transformer size is 800KVA
THIS CALCULATION IS EXACTLY CORRECT
BUT FOR FUTURE EXPANTION WE CONSIDER 30 % MARGINE FOR THAT
Is This Answer Correct ? | 80 Yes | 13 No |
Post New Answer View All Answers
at work i have a genertor/alternater what is the easyest way to work out if it is dc or ac?
How we can calculate the consumption in kwh of motor on basis of kw @100% load, @50% load & @ no load.
What tests should i carry over on a newly rewinded DC Generator with voltage rating of 38 volts and current rating of 350 amps, to certify that the machine is OK?
operation of diesel generator
how to commissioning the genset with amf panel?
What is meant by Low Resistance Cable and High Resistance Cable.
Can u tell me design of switch yard
Some times to change of DOR of a motor, interchange of R & B is not effected and RYB take same current, but interchange of R&Y is effected ie change the DOR. My doubt is what is the problem in motor and how it is happen.
How you give clearance to a spare feeder.
how to calculate the loss tangent of electrical cables
WHAT IS DEGREE OF COMPOUNDING IN D.C MACHINE MEANS? HOW TO READ THE OPERATING CHART FOR ANY ELECTRICAL MACHINES?
WHAT IS THE DIFFERENE IN ACTION OF MCB,MCCB,RCCB
A 2083kva AVR was tested, phase to ground shows continuity, what is the implications
when measure the core loss of three phase distribution transformer or three phase reactor loss, one phase shown negative watt loss. why??
What is voltage ratio of a transformer?