what type of relays used in transformers?
Answer Posted / minal
Bucholz relay is used in oil filled transformer.These
relays sense the gas & trip the transformer before a fault
is occured.
Indoor type of transformers(without conservators) are
equipped with sudden pressure relays, which performs a
similar function like bucholz relay.
Is This Answer Correct ? | 32 Yes | 3 No |
Post New Answer View All Answers
What does ampere turns shows?
The D.C. spark test is applicable to single conductor cable & assemblies of insulated single conductor cables without insulation shield,metallic sheath or metalic armor?
i am going to correct power factor of 1600kw induction motor,when i calculate capacitance of capacitor it is three time more in star connection than delta. if motor is star connected which connection i shall adopt for capacitors and reason for adopt this connection
what is zinc diffusion?
Which standard we are following earthing resistance test
What is the reason behind current flow(20 A) in amain earth cable of an SMDB? Is cuurent flow(45A etc) through a neutral cable acceptable?
What is mean by spike arrester(Voltage Operated)
What is the control action?
1sq mm dc powr cable can carry how much dc currnt
what is earth resistance? how to measured? and give values at power station and mcc area?
What is precision of a measurement?
what is basic difference betmeen normal & flame proof motor??
Write down the design procedure of commutaj.
How can we choose the rating of submersible motors
What happened if C.T mount at any cable or Bus bar in wrong direction . C.T going on proper work or not . C,T direction is essential thing to properly work.