what do you mean by 1 ton in AC`s
Answer Posted / s.pushparaj
The amount of the heat required to convert 1 ton (2000
pounds)of ice in to water within 24 hours. The initial
temperature of water is 0 deg C.
Latent heat of ice= 144 BTU
1 TR= 144 X 2000
= 288000 BTU/24
For 1 hour
We can divid by 24 So 288000/24=12000BTU
1TR=12000BTU/Hr
=3024 K Cal/Hr
= 12600 K Jul/Hr
= 3.52 HW OR K Jul/Sec
Is This Answer Correct ? | 89 Yes | 12 No |
Post New Answer View All Answers
What is Control & Relay Panel? And Remote Control Center?
Can anybody inform me about the pattern of ECIL GET( Graduate Engineers Trainee) interview for Electrical students? Will there be HR round as well? I thought of preparing for 2 to 3 subjects thoroughly. Will it be sufficient? Please share your thoughts.
What is meant by Im=30mA@Vk/2. How to know the kee point voltage for CT design
The moisture in air will condense at
reason of diode failure in alternator
How can we measure the residual voltage in dc machines?
I have a relay contact rated at 220v dc which is supplied with a 24vdc from the panel,for it to trip the dampers(24vdc).What if the application of the relay changes so that it should work at its rated 220vdc then will it work at 24vdc supply given or any other consideration needs to be taken .....
why does rotor rotets?
what is basic difference betmeen normal & flame proof motor??
State the other types of Air Conditioners?
2. What are the parameters of EHT sub-station?
How much minimum insulation required between 11kv/3.3kv transformer windings?
Details about Flux Compensated magnetic Amplifer starter for motors
What type of a DC motor would you use for a lift?
10 tube light connect in mcb breaker.one tube light is fault.so breaker is tribe.how fault is rectified.(using 3wire phase,earth,neutral)