What is the diffrence between an ELCB(earth leakage circuit
breaker) and RCCB(residual current circuit breaker)?which
has higher degree of safety and why?
Answer Posted / rvg
ELCB having protection against earth faults, but RCCB having
over current protection as well as earth fault protection.
So RCCB having higher degree of protection.
Is This Answer Correct ? | 20 Yes | 5 No |
Post New Answer View All Answers
On what basis the the size of Lightning arrester for buildings are selected ?
Transformer diagram mention each parts ?
WHTA IS LIMT OF LEAKGE CURRENT OF 11 KV 1 CORE 1000SQ.MM. XLPE CABLE.LOAD ON CABLE IS AROUND 600AMP .LENGTH 500 MTRS.
Name the component u would expect to find in a switchgear assembly?
What is ramp signal?
How many methods use the load flow solution?
What will be the effect if I use inverter as UPS mood?
Whether IP65 enclosure box blocks ventilation if driver for LED have to enclosed inside IP65 box
slipring induction motor starting time Lrs operating why lrs starting time lrs outer body didn't get shock
What is different between Difnit time and instatous over current relay
What is touch potential and step potential?
excitation limit of an excitor
how pt is using
How to calculate per unit impedance of transformer?
Draw the wave shape of armature current in a generator subjected to a sudden three phase short- circuit at its terminals. Define various reactance of generator from this wave shape.