what is ELCB?

Answer Posted / shanmugam.a

ELCB - Earth Leakage Circuit breaker. Its means, whenever,
the Earth leakages( N&E Amps) is higher than the breaker
rated mA, the breaker will trip automatically. Especially,
it will provide for the single phase circuits for more
protection to the human being ans equipment safety.

Is This Answer Correct ?    41 Yes 5 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Why let through energy not considered for ACB breaker while cable sizing?

1872


why occ characteristics of generator is also called as magnatization characteristics ?

1503


what are safety measures in /control in diesal engine/ explain them?

1355


What is industrial plc

1313


what is meant by poly phase induction motor ? how its operating by single phase or three phase?

1732






How to calculate Number of Earthing Pits....???

1127


in what type of applications v can use q meter?

1673


What is Traction? 1KVA Alternator, How much urrent taken?

1606


1600kva capacity Transformers how the bucholz relay,Oil temperature,winding,surge relay relays setting are to be done

1486


Dear sir, In our plant have Station Transformer having capacity,i want to know, why LV side 40 - 40MVA is given? & how we can get 6.3 KV supply from tertiary(i.e. Open delta connection), Vector Group YNyn0 - yn0 +d MVA Rating 80MVA / 40 - 40MVA + 26.7MVA Voltage rating 420 (Tap range +6,to -10)81.25% /11.5KV - 11.5KV +6.3KV

1759


Scott connection is used for A 3-phase to 2-phase conversion B to achieve higher effciency C to save copper D to reduce harmonics

1872


all details of DG UPS HVAC

1540


whati s the sludge current in ups

1704


Difference between On Line capacitor and Station Type capacitor.

1629


how can motor both beasrings insulation resistance can be check?

1558