how to calculate knee point voltage of current transformer?
Answer Posted / saleh abdulsalam trabelsi
to calculate knee point voltage of current transformer by
formal
Vknee point = Isecandary(Rct+ Rcable+ Rburden)
where
Rct= resistenc of current transformer
Rcable =resistenc of cable =2Rcable
Rburden =burden of relay
IF Vknee point< manufacture voltage of current transformer
current transformer is good
IF Vknee point> manufacture voltage of current transformer
current transformer must be change
| Is This Answer Correct ? | 88 Yes | 47 No |
Post New Answer View All Answers
If we need4× 50mm sq cable but it's not available so we can pull 4×25mm sq 2cables
what shall be no load voltage of 132/33 kV transformer ? is it 33 kv of 34.5 kV
WHY THE COLOR OF OUTDOOR TRANSFORMER IS BLUE ONLY???
What is Anemometer used to measure?
How to calculate the sag of OPGW during stringing???
2- What are the percentages between excitation currents in phase (R, S and T) in ∆ and Ỵ connections in excitation Current test in transformers?
define reflection method?
what is the difference between an alternator and a synchronous motor
how hydrogen cooled alternator undergo maintanence ? that is hydrogen when come in contact with air can result into explosions .
Why hydropower stations are preferred solution for meeting peak loads in grids?
Which cable is use for rtcc control panel
Define the term factor of inertia.
ELECTRICAL DRIVES: can a motor load system with passive load torque can have equilibrium speed in second quadrant
How to calculate the Efficiency of Chiller
Can the output voltage of a rectifier be greater than the input AC voltage without the use of any voltage multiplier in the circuit??please provide the explanation too..