What is the reactive power and how to control the reactive
power in power plant
Answer Posted / m.mousa
We could define the reactive power if we how it generates
as follow.
All inductive (i.e. electromagnetic) machines and devices
that operate on AC systems convert electrical energy from
the power system generators into mechanical work and heat.
This energy is measured by kWh meters, and is referred to
as “active” or “wattful” energy. In order to perform this
conversion, magnetic fields have to be established in the
machines, and these fields are associated with another form
of energy to be supplied from the power system, known
as “reactive” or “wattless” energy.
| Is This Answer Correct ? | 52 Yes | 13 No |
Post New Answer View All Answers
WHY DO VOLTAGE TRANSFORMERS FAIL DURING EARTH FAULT IN THE DELTA CONNECTED 6.6KV ELECTRICAL SYSTEM
how does an encoder work???
Why line VTG = √3 phase VTG in star? How?
Why use the vcb at high transmission system ? Why can’t use acb?
What are the main faults of DC generators?
Why wind turbines wheels rotate constantly
How to calculate KVA/VA rating of PT or CT from primary & secondary voltage or primary & secondary current?
wht is embedded systems? what is new inthis field?
What is a differential amplifier? Also, explain cmrr.
state types of reflectors in illumination engg. ???????
What is the difference between hot and cold loop testing?
What is the function of Governor in Hydro Power Station? What is the Function of Lightning Arrestor Voltage Transformer (LAVT)?
What is knee point voltage of transformer?
How can claculate to attain the desired PF in the line ( HOW Much KVAR is required ) Pls Give the formula? Equate Petrochemical 0 1 how to calculate sizing of NGTR (Transformer rating,Loading resistor value and Current rating of resistor) and what is the X/R ratio. Details : 11kV,Capacitance 1.73532 micro farads,40kA for 1sec. 0 1 What will happened. if we feed 3phase supplay to the stater with out insert the rotor. How much current will flow through the stater winnding? Equate Petrochemical 0 1 What is required of exietation to the alternater. 0 1 why star point of HT motor not earthed? Equate Petrochemical 0 1 Why we are getting low voltage in star connection? Equate Petrochemical 0 2 What's ND relay & it's functions? Equate Petrochemical 0 2 How instantanious short circuit current is calculated? its formula? Equate Petrochemical 0 2 What is servo Motor? What's the advantages of this motor over Induction motor? Equate Petrochemical 0 2 What is core CT & it's function? Equate Petrochemical 0 3 what is meant by star/delta voltages as 440/220 in a 3 phase induction motor, and why it should be connected on STAR IN 3 PHASE SUPPLY L & T 0 4 What is required of exietation to the alternater. KNB 1 23 what is the design voltage for 6.6KV 2000 KVAR HT capacitor? Consultancy 0 3 Pls explain about vfd control?Where it is used, Give some example? siemens 1 22 Please explain me abt PQ diagaram in the power sector. 0 9
WHAT IS THE DIFFERENCE BETWEEN GENERAL INVERTER AND SOLOR INVERTER TELL ME PLZ