where we use zero sequence current transformer or core
balancing ct.

Answer Posted / blake australia

To detect earth faults:
Zero sequence refers to the current flowing during an earth
fault. 2methods of decting earth fault.
-Measure the current on the earth return cable
-Measure the current imbalance on the 3x phase cables (do
this by putting all three through the same core balance CT.

Is This Answer Correct ?    24 Yes 5 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what is cause of static electricity? I experience shock when i touch metal equipment in a room ,furher check shows earth leakage showing 80ma at the DB near to the 400 MCCB?

1457


ho can we calculate the conductor insulation value according to their ratings like voltage,current etc.how insulation value related with voltage,current and power of amachine

1580


What is a dominant pole?

681


What is the maximum and minimum rating of UPS?

1002


ANY ONE TELL ME ABOUT generator synchronization panel panel to synchronise 3 gen of 250kva both automatic and manual. 2 gen output vol 415 3ph, 1 gen output vol 400 3ph SEND THE DETAILS DIAGRAM ON THIS EMAIL ADDRESS ayazleo@hotmail.com as soon as possilble best ragrds electrical engineer ayaz mahmood SAUDI TECH

3704






can i connect the two phases of scott connected transformer,if not why?

1511


What is real time power factor control panel(RTPFC)?

3830


how many types are their in switchyard or substation(like D,I TYPE), what is differant between them

1661


What type of core material is used for metering C.T and protection C.T???

1690


difrent between vcb acb sf6 and mccb breakers

4606


what is solkor relay and which condition it will act?

2860


generally in LT and MV motors we are using 3.5Coresx16,25,35,50 etc cable for supply.although motors is earthed at two point and having all protection.then why we are using that 1/2 core for earthing the motors.while in HT cable we are using only 3core cable for motor supply.generally lt and mv motors are delta connected and ht motors having star connection.whethere it is having any relation with winding connection( star or delta).all motors i am talking about are dol only.can anybody solve my confusion.thanks...

1544


what is PWM in IGBT and how it works for drive.?

1232


how circuit breaker work.. what is the operations taking place inside a circuit breaker when an overcurrent occurs... is it similar to fuse?

1618


1 “earthing” for bonding of equipment and circuits to common plant earth electrode potential, 2 “protective earthing (PE)” when this bonding is required for personal safety provisions 3 “grounding” for interference suppressing bonding of screens, sys-tems with ground level 4. low-impedance earthing ? 5.primary earthing system and secondary earthing system what is that? 6.earthing electrode or mesh net earthing electrode ? very confusing , simple but very informative help required ? i will be very very thankful to you guys.

1604