What is C.T, why it is used and what care should be taken
for that while connecting?
Answer Posted / pankaj desai
CT is Current Transformer which can be used for both
options either for measurement of Current or for Protection
system.
Secondary of CT should be shorted all times as high voltage
will be generated which may be harmful for the person
working on system as well as to the system where CT is in
use & damage insulation.
| Is This Answer Correct ? | 3 Yes | 0 No |
Post New Answer View All Answers
What is the importance of earthing?
How can I known multiplying factor .without multiplying table
which is better to use svc or synchronous condenser why ?
draw the block diagram of fire alarm?
There is air in a room . the top and bottom of the room are at constant temp. T1 and T2. DRAW THE temp profiles if a. T1 greater than T2 b. T1 less than T2
DG Earth Value?
how do you choose the cable size as per amps rating & the voltage drop for the same.
Hi,I am working in abroad for more than 3 years in a company operating with 11kv and 6.4 MW power. I need c licence in India,can I? some other says only i can get if i work for 2 years in india only! anybody kindly clarify by doubt.Thanks
Explain Need of a starter in a dc motor.? Also explain any two starting and speed control method of dc motor?
In layman terms, what is the difference of Dielectric strength and dielectric constant when speaking of an insulating oil
Why to keep capacitor bank off while generator running.
STATE USE OF ARC RUNNERS & SPLITTERS ?
What do you mean by ratio correction factor of instrument transformer?
Explain the method to keep noises low in a control system?
How to calculate of maximum demand if given 628kw, 785kva, 0.8 p.f.