What is PF? Formula for calculating PF in HT side?
Answer Posted / nagesh.patwari
It is ratio of True Real Power to Apparent power.
Cos phi = KW/KVA = R/Z = True Real Active Power / Apparent power
KW = sq root of 3 x V x i x Cos Phi
hence cos phi = KW / ( sq root of 3 x V x I)
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
What is minimum permicible value of leackage current for LT Panle when applying voltage up to 3 KV for 5 Minuits?
What is the disadvantage in proportional controller?
How 48-relay (incomplete sequence) functions?
Is it acceptable of installing an earth pit in planters area where bare copper cable, earth rod and connection are susceptible to corrosion due to water?
What is the reason for using a GE G101 MCB in place of an EP102 MCB if both are capable of AC circuit protection?
how we explain parallel paths armature winding?
What is state space method ? Why its used ? Can it applicable on linear, non-linear, 1st order, higher order, homogeneous, non-homogeneous, open-loop , closed loops , stable & unstable systems ?
how to prepare the technical test
What is the meaning of C1, C61, C91 cable
Define demand factor?
What is the difference IN MCCB's between thermal magnetic and electronic tripping system ?
How to convert a two phase power into a three phase power in induction machine?
Are Refrigerators & Deep Freezers the Inductive load ? How to calculate the Power Factor & hence the Output Power for them ?
take 100kva DTR( delta/wye ), what ll happen if we connect 11kv to LT side instead of connecting to HT side? will the DTR behave as a step up transformer or something else????
Do Phase angle measurement have any application in freq/harmonics measurement? If so how?