how we can know the rating of transmission line by no. of
insulators disk ??????????
Answer Posted / mitesh patel
The 400 kv transmission line required no of disc ppt the value this formula
Value of voltage (KV)
N = KV/19.03
Then add 1 disc . Fore exmalpe
400/19.03 = 21.01~ 21 + 1 = 22 disc required
Is This Answer Correct ? | 6 Yes | 3 No |
Post New Answer View All Answers
EXPLAIN USE OF ROCKING ARRANGEMENT IN ELECTRIC HEATING?
armature is that part in which current is induced since in dc motor we supply current to the conductor so why we call it armature?
Write the current equation in series RLC circuits.
which cable is used for 15 Hp monoblock pump 3phase and service wire Distance is 210 feet please tell me cable size Armaured
redundant connection in contactor?
If breaker is undefined position, first step to do.
Why the dc voltage drop during starting of emergency lube oil pump? The Voltage drop from 135kv to 125 kv for one min. before re-establish to 135kv?
What is dc current source? Differentiate between ideal and non ideal current sources?
1 Ton is equal to how many watts?
What is power relay?
What is the difference between line drop and percentage line drop?
what is the necessity of under ground cables ??
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating
In HI POT test what is reason for applying the AC VOLTS and DC VOLTS in different applications what is the nessesity for this ?
What are the advantages of autotransformer?