1.Is there any difference between terminologies,HT-HV <-
LV?
2.What is the highest transmission voltage level in india?
Answer Posted / c.a.chokkalingam
As per India-IE Rules, Below 1000Volts is Low Voltage-LV & Above 1000V is High Voltage HV, When referring to Transmission Lines, Each line being stringed in Tension to withhold the weight of ACSR Conductor, hardware accesories & Current carrying with in, TLs are given in terms of HT or LT [11KV, 132KV, HT Line]
&
Referring to M/Cs it’s mentioned in terms of HV or LV [for an instance: 990KW, 11KV Ring Granulator]
There is one other Voltage Level-EHV or EHT, Above 132KV are EHT[ 220KV, 400KV & 765KV as such max. in india]
Thanks,
Chokkalingam
Plz let me know if there is any update.
| Is This Answer Correct ? | 3 Yes | 0 No |
Post New Answer View All Answers
Why you want to join non technical field when you are an engineer?
in power generator normaly voltagr betwween esth to neutral is 0 but my work place generator show the volatge is 60v any body know why? thanks
What is the drawback of class b amplifier? How is this minimized?
When we use 3 terminal resistor?
Why transformer used in UPS??
Is a contactor (or master relay) required between incoming lines and a VFD? The question goes to safety. If a contactor were used before the VFD and an e-stop engaged then the motor will coast to a stop (i.e. VFD loses power) instead of stopping much faster if the VFD braking fucntion were used. It would make more sense to keep power on the VFD.
What is the purpose of stand by earth fault protection for transformer ?
Can you explain about TEE protection scheme?
Hi My dear all Friends, There is a question regarding HVAC Engineering and widely used in Power Projects. Question- What is the diffrence Between REF, SEF and Differential Protection....???? Where REF - Restricted Earth Fault SEF - Senstive Earth Fault.
how many current required for hypo test
RESPECCTED SIR/MADAM- I AM PRERING FOR SECTION ENGINEER (ELECTRICAL) RRB CHANDIGARH PLEASE SEND ME SOME PREVIOUS YEAR QUESTION PAPER OR MODEL PAPER.MY EXAM IS ON (30- NOVEMBER 2008).I AM VERY THANKFUL TO YOU. FROM- HARENDRA SINGH YADAV
what is RNG in the DG synchronizing by PLC?
how can i use REF and diffrencial relay both in 1 CT core for transformer protection?
hi friends how 3 phase converter functioning ?what is working principle of rotory phase converter ?
Ceiling Fan and Storage type water heater. Discuss