In which principle Woodward Governor 505 work in power
plant? What are the input of Woodward governor 505
Answer Posted / praveen kumar
Governor input is RPM....and based on setpoint it give 20-200ma to servo actuator, it increase actuator open or closing based on the setpoint and process variable(rpm) errors...its a simple controller oly...but the output range was changed....
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
In my company plc based winders are operated. one day there was a data transmission failure alarm shown on pc. as per sir instruction we have reset master plc but winders were not triped and alarm gone. so what master plc do?
What are the error values can accepted in flow transmitter calibration?could u give any formula for this?
what is instrument philosophy
Working principle of magnetic flow meter ......and calibration procedure of e+h magnetic flowmeter...
What is the purpose of bypass valve across AS valve.
how to control pid
How to calibrate level transmitter with use of HART?
how will you check torque value during Factory acceptance Test for control valve/ESD ON/OFF VALE how will you confirm this torque value is being correct, Which document will you be refer.
Why upper weighing limit of electronics balance is 90% of the total weighing capacity?
What is the differerence between hysterisis and linearity.
HI, can anybody give details about GAS TREATMENT PLANT CONSTRUCTION,as INSTRUMENTATION ENGINEER what are the responsibilites.what are the instruments mainly instrumentation engineer will deal with
i have done DAE in Instrumentation and Process Control. i have applied for an apprentice training in chemical company after three day my interview will be conduct but i need more information about industrial process control and controller. my e mail is imran_dilsetu@yahoo.com please tell me interview question relative to instrumentation ?
how 3 out of 2 Logic/interlocks works? give brief explanation with help of diagram.
How u measure the massflow in orifice flow measurement techniques
what are the diff. in servo and regulatory control?