Can be ammeter and voltmeter used without CT? if not, what is the reason for that?
Answer Posted / sameer
if you are measuring current at the high voltage line have current 60Amp then you cannot connect the ammter directly you have required CT whose scondary is connected with the ammeter . same as for voltmeter if range beyound 750volt measure you need to connect voltmmeter to Pt
| Is This Answer Correct ? | 9 Yes | 1 No |