There is 15 KVA UPS using for single phase load.And 30
batteries of 12 V, 100 Ah are connected in series. Load is
taking 15 A current.What will be the back up power for this
UPS on same load?

Answer Posted / k.prakashchandra

Is it correct that batteries are connected in series ? The stored energy in each battery is 12 x 100 = 1200 Wh. Total = 36000Wh . The load in watts = 230 x 15 = 3500W ( app ) . Back up = 36000/ 3500 = 10 hr(app)

Is This Answer Correct ?    2 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what is allowed value of zero sequence impedancce of 6.6 kv nuetral earthing transformer ?what is the actual value

1647


12.5 tons a/c is their how much kva generator can recommend to the customer.

1478


what is a speed of rotor when we give supply to stator of 50hz and as well as rotor of 60hz of an induction motor?????

1224


Hello seniors m an engineering student in 3rd yr..i want to know what are the software course in electrical field?i wanted to do certification course but i dont know much about the course?..Regards

1650


What is the unit of charge and current?

618






If a air condition consume 2.50 to 3.00 amp then how much it will consume in watts if it is running 10 hours out of 24 hours????

1441


what is meant by tranformer impedance?

2156


i have install 750 kva distribution transformer at my site and want to do neutral earthing. what calculations should i follow to determine earthing conductor material and size?

1572


when we have to purchase the transformer by own i.e how much load will preferred HT connection?

1191


how to check ac servo motor

1714


what happen if the parallel generator phase angle shift by 1 degree in manual mode

1558


which book to refer in electrical engineering for iocl exam & which book for general english.

1759


Explain (in simple ) - root mean square. whats its role in electrical fundamandal.where its used

1802


I WANT TO INSTALL LIGHTING ARRESTOR ABOVE 20 FEET HEIGHT INDUSTRIAL BUILDING. NOW IT WAS 15 FEET HEIGHT HOW MUCH DISTANCE IT WILL COVER & HOW TO CALCULAT THE DISTANCE COVER BY THE ARRESTOR

1492


why the colour of insultor stack , petticoat is brown. Is it has some technical reason.

1569