What are the tests to be taken on a transformer and
generator?
Answer Posted / vipul parmar
1.Insulation Resistance Test
2.Winding Resistance Test
3.Magnetizing Current Test
4.Magnetic Balance Test
5.Voltage Ratio Test
6.Open Circuit Test
7.Short Circuit Test
8.High Voltage Test
9.Double Voltage Double Frequency Test
10.PI Test
11.SFRA Test
Is This Answer Correct ? | 2 Yes | 0 No |
Post New Answer View All Answers
what is sustainable current of any conductors . a bare busbar or pvc cable has different sustainable current .
Can we transmit digital signal to long distance ?
what is subtransient , transient and steady stateac components
RATING OF LIGHTENING ARRESTER FOR 11 KV LINE IS 9 KV is ok ,but haw to calculate the KA rating?
I have doubt that the supply HZ (very low or high than rated ) may affect the power factor. is it true. ?
What cmos is and its benefits?
Please explain the following and how these are working with PLC unit 1.I/O Module 2.I/O Device 3.Adaptor Card 4.Ribbon Adaptor 5.RS 485-FC
How to Calculate The Neutral Earth flat design calculation for the Synchronised generator (Gen 1-650Kva, Gen 2-725Kva
how many types control panel of a 132/33 kv substation
The principle of switching circuits for different types of batteries in application of storage systems
How do apply electrical 'c'license......pls advice
what is earth resistance? how to measured? and give values at power station and mcc area?
How much minimum insulation required between 11kv/3.3kv transformer windings?
wat is the current produced in a 5000v megger? when the positive and negetive terminals are touched on our body get s shock?
Which type of air compressor is used now a days in the market. Keeping in mind of energy efficiency and maintenance points. Relevant documents may also be sent on mentioned email ids.