what need of NGR(neutral grounding registor)? What it works?
Answer Posted / murafiq
NGR used for limiting the ground fault cuurent that is
installed in between generator neutral point and earth in
case of fault that limit the fault current that is of
diffrent type resiatance type, reactance ,petrson coil
earthing. In case of one phase fault that NGR limit the
current and relays detect that and trips the generator.
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
how to work droop ct in generating station
what is the difference between oil surge relay and buchholz relay.
A 10 MVA, 66KV, 50Hz, Y-connected 3-phase alternator has synchronous reactance of 0.635 Ù. It is working at full load at 0.8 lagging p.f. condition. Find torque angle, neglect armature resistance.
What is q factor?
How many wall/floor flange will i use in bus duct system if we have in our design a 35th floor building.
Why you are switching off arc protection mcb when you are taking shutdown for lv board.
In PFI plant one stage capacitor connection is directly connected(with out megnetic contact controll). but why?
What is turn ratio of a transformer?
If the rated speed of a d.c. Shunt motor is1440 r.p.m, which method of speed control would you suggested to obtain a speed of 1500 r.p.m?
What is the requirement of grounding the neutral of single phase generators on load? If the neutral is not grounded, what will be the effect?
How much weight an electrical engine can pull??
what is the difference between droop mode and ischnorous mode in thermal powerplant?
How can i calculate the Breaking capacity of molded case circuit breaker, is the breaking capacity of CB for Diesel generator shall be less than grid supply's breaker ?
Is there any Institution for giving M-tech in Electrical engineering for those who r in service? Give the details please.
defination of lines