what is the main purpose of line PT and bus PT?
Answer Posted / v.doraiswamy
Line PT:The Line PT is located on line side of the Feeder.
This will have normally has two secondary cores.The core
with accuracy cl.1 is used for metering purpose(ie)
measuring Voltage,watt,var etc. Core with accuracy cl.3P is
used for Porotection like distance scheme relay,
directional O/C,E/F relay. Also metering secodary core is
used synchronising the line with Bus.
Bus PT : The Bus PT functions are same as Line PT. But This
is located on the main Bus and this can be used for all the
circuits being located in the Bus. For cost point of view
it better to have common Bus pt for all the circuits.
| Is This Answer Correct ? | 13 Yes | 5 No |
Post New Answer View All Answers
What happens if the Capacitive Voltage Transformer Primary neutral is not earthed. There is a CVT between Transformer and source, and the CVT neutral of the transformer is not earthed, does it effect the transformer while charging or does it effect the transformer charging process.
what is a pilot wiring and whys that called a pilot wiers
Please explain the following and how these are working with PLC unit 1.I/O Module 2.I/O Device 3.Adaptor Card 4.Ribbon Adaptor 5.RS 485-FC
What do you mean by per capita requirement of electrical energy in india
the grid connection required for a 50 MegaWatt fotovoltaic powerplant is higher or lower than 35kv (high or medium tension)?
What is resonant peak?
I have c license but I don't know eligibility of Max Kilo Volts under the electrical licensing board.
List the advantages of star-delta starter with induction motor?
How will change the frequency in distribution side?
There is air in a room . the top and bottom of the room are at constant temp. T1 and T2. DRAW THE temp profiles if a. T1 greater than T2 b. T1 less than T2
if we have 320KVA Genset kindly advice how much load we can put it.
Actually I have a doubt on neutral and earth.we use Ac power without taking neutral by connecting to earth,but at that time does it affects on efficiency of any electrical components or no? If yes how?
Can you tell me more about pu systems (per unit systems )calculation in large power systems? how to get the base for voltage and power in generator, transformator and transmission lines?
sir i am apearing for nic exam.i dont know exam pattern.can you please send me some model papers
what is the current setting for different relay protection for transformer .