Relation in between KWH & KVAH for Electrical consumption
unit & how we can relate if KWH is lower than KVAH
Answer Posted / rajasekhar
KWH is energy consumed for useful work.
KVAH is the apparent energy from source.
if kwh is lower than kvah then it might be a lagging load or leading load.... but not resistive.
| Is This Answer Correct ? | 101 Yes | 13 No |
Post New Answer View All Answers
How to calculate the input cable rating for 10kva ups (3phase input and single phase output and also 3phase output, battery rating 65Ah)provide the formula also.thnx
Is there any type of starter for DC motor other than two point,Three point and Four point starters?
What are the factor to be consider for CT selection in 132kV substation?
What is the difference between UPS & inverter ? which UPS is better and whos got the edge ? what is the difference between & inverter ? which UPS is better and whos got the edge 12 V , 24 V , 36 V etc what are the advantages of 12 V, 24 V , 36 V etc and what are the disadvantages of 12 V, 24 V, 36 V etc thanks
can u describe the method used for protection of transmission line.
What is proportional controller?
We have a couple of oil tanks at our plant. One of them does not have a lightning arrester installed. My question is it necessary to install an arrestor on every tank or will this particular one be covered by the arrestor installed on the ajdacent tank, Since all the tanks are close to each other. Basically, I want to know that if these arrestors or protection works in a parituclar area of effect or influence. Thanks
how can I calculate charging current of cable/overhead conductor? what is roll of voltage in it ?
placement paper samples of mspl company
What is voltage ratio of a transformer?
How to select HT/MV cable size ?
why different series of vfds (like allenbradley)are used in industry ?
Pls explan the OLR setting in VCB at HT yard
What are dcs and plc?
what is the value of combined earthing in general electrical circiut?