What can be a rating of a transformer(KVA) if the load is
about 1000KW?illustrate by showing formula?
Answer Posted / abdulwahab m. khamis
the answer is 1500 kva
kw=pf*kva if we consider pf=0.8 then kva=1250,multiply this
result * 1.2 for starting equals (1500 kva)
| Is This Answer Correct ? | 7 Yes | 0 No |
Post New Answer View All Answers
Can we use both Electrical & mechanical interlock between tow breakers? if yes how, please explain
what is the setting of locked rotor in HT motor ? (answer expecting in percentage)
Can an inverter be used as a converter? How?
How can we calculate cable size in Low voltage & high voltage
How can we calculate the motor frame sizes?
how load of a turbo generator can be increased
Why is water motor not taking the pressure? what is the problem?
What will be the current if the resistance total in a series circuit doubles?
why the check zone and main zone are used for Busbar Protn. scheem?
What is the formula for calculating the Instantaneous Short Circuit & overcurrent for any breaker
How will polarity test of Dy5 Transformer ?
what irequirment need to be followed when working on live equipment
How do i carry out or know the vector group of a Dyn1 and Dyn5 transformer
STATE USE OF ARC RUNNERS & SPLITTERS ?
If I want to lift the water at a height 50m from ground level through two inch(diameter) metal pipe then what is the capacity of motor pump is required? is it possible in single phase supply or not?