In a 3 phase induction motor(without connecting supply) if we
rotate its rotor by hand and check resistance of stator
winding at motor terminal box its resistance varies why ??
Answer Posted / k.prakashchandra
Probably due to the voltage induced by residual magnetism of
the rotor
| Is This Answer Correct ? | 10 Yes | 5 No |
Post New Answer View All Answers
what is conductor copnstant of ab cable
hi Is there any possibilities to find out the rotation of a shaft or something else by using electromagnectic waves or by IR rays.If s then can v change the dir., of rotation of the same by remotely?& how? plz dn't any1 say "NO r CAN'T"
CALCULATE THE TOTAL VOLTAGE DROP AND SELECT THE CABLE SIZE IN MM-SQARE FOR A PANEL-262KW AT 110 METER FROM THE SOURCE SUPPLY , SUPPLY VOLTAGE 240/415
A cable with concentric PE conductor must be used with frequency converter circuits what does its means.?
How to distinguish whether MCB is DC or AC looking at it physically
when will be the iocl interview results i faced interview on 8th september 2008 iam from electrical branch i faced interview for the post of electrical engineer??????????????????????//
if negative of DC supply used and positive is grounded through EGB, and if ELCB used in the system then is it sense the positive volatge and get tripped is it possible?
what is residuel magnetism. and how order lead acid batteries for 24 volt. emergency lighting system.
Why it is necessary to isolate fire fighting when you are taking shutdown for lv board.
what is die electric strnth of transformer ?
What is the use of Surge Capacitor in LAVT?
What is the difference between rated and per unit in transformer?
What is error of a measurement?
In between UPS out going changer over switch and ups raising main input, both side cable gland producing heat but the cable doesn't get heat,Why?
what is the meaning of osr in transformer.