how to calculate knee point voltage of current transformer?
Answer Posted / shakir mehmood
The formula for Knee Point Voltage is:
Vkp = K * If/CTR * (RCT + RL + RR)
in which,
K = Constant, conventionally taken as 2.0
Vkp = The minimum Knee Point Voltage
If = Maximum Fault Current at the location, in Amperes
CTR = CT Ratio
RCT = CT Secondary Winding Resistnace, in Ohms
RL = 2-way Lead Resistance, in Ohms
RR = Relay Burden, in Ohms
| Is This Answer Correct ? | 31 Yes | 5 No |
Post New Answer View All Answers
Explain in details how you would react to an unexpected incident when your supervisor or manager is not around to give instructions?
hi, could someone help me to find a control design for syncronising panel .
whatare the disadvantages occur,if the form factor of transmission will not be equal to 1.11
what are the maximum available current, voltage ratings and switching speeds of the power electronic devices thyristor, power mosfet, igbt, and mct?
What is the rating factor for copper cable ( Specific value according to the type of laying ) & the voltage drop?
what is the use of current transformer in power transformer secondary side.?its connectyed in WTI
What happens to a motor if it is connected in Delta connection
Usually in the L & T make MCC feeders' power circuit,we have BMR after the MAIN CONTACTOR.,can we interchange their position, keeping the control logic same???
What happen in ups if phase reverse?
while doing high voltage test on 11kv/433 distribution transformer why we only give 28 kv on hv side and 3kv on lv side for power transformers what is the value what factors it depends
how to remover corona effect and hysteresis losses from contactor
i am trying to PSUs/govermeant jobs since last 2 years but still i m not success, plz help me.
What is expention fastener (Fan)
What is the equivalent circuit of a transformer and its vector diagram?
in my industry we are using 3 step up transformers for induction heaters..i.e 415/580v and other are 11/440v.in power consumption does a step trnsformer makes any difference compared to step up?? plz explain