What is the difference between online ups and offline ups?

Answer Posted / vinay srivastav

On line UPS gives out put through inverter card out put at
all time AC supply on or off. That means UPS always on and
gives AC out put which is converted from DC out put of
Battery voltage. But the Battery life in this type of UPS is
low as compare to that of offline UPS.

But offline UPS gives out put only when commercial supply is
off. commercial supply directly given to the load and when
commercial supply fails UPS feeds the supply to load. That
means UPS is not connected to load at all the time. In this
case battery is not connected all the time so the battery
life is more as compare to online UPS

Is This Answer Correct ?    1 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

stand by earth fault protection (51G) for transformer rating 2000 kVA,Dyn11,33/0.400 V. LV NCT ratio and necessary resistor and metrosil values how to calculate

2191


can a 150 kva 3 phase 440v/230V delta-wye step down transformer can be use as step up transfoermer with connected loads at 440v side?

1259


what is buffer resistance starter.?.What is the working principle and where it is used..?

1562


hai...... tis is Hemanth. jst now completed electrical engineering... i wanna to apper for ap tranco exam... plzz send me the previous q's paper link......thanx in advance.

1583


How to arrange a hous hold earthing system to keep minimum earth resistance( below 7ohms).

1488






What will be the effect of circulating current in HT xlpe cable when both the armour ends are grounded. Will the termination fils after some time in case of 33 kv supply.

1625


How earthing/grounding done in aeroplanes and ships.

3121


Where should the lighting arrestor be placed in distribution lines?

662


What will be the size of copper cable (each for 3 phase and 1 neutral) from Service connection Kit-Kat to Panel Board (i.e. to main switch) for a 6 pole 3-phase AC induction motor of 200 H.P. capacity? Amp-255 A, Frequency:- 1450 rpm.

1496


How each of the following losses occur in d.c machines (i) copper (2)core (3) windage (4)friction please help me

1591


Explain the experiment on ward leonard method of a speed control on a dc shunt motor with an suitable circuit diagram.

2103


How Can I calculate for the photometrics requirements for a street lighting? Data given are: 45 units of 6 meter light pole with 150 watts metal halide lamp, 220 volts and installed in a promenade area.

1416


please write motor, transformer, Generator setting, fault level calculation of Tr.etc

1516


what is auto re-closer?

1992


What is the tests required for a 132 kV, 400 kV , 765 kV for a Circuit Breaker and Power Transformer before commissioning ?

1163