how much amp MCB is required for 1/2 kva power back up?
Answer Posted / shantanu
Look 1KVA = 1000VA
Therefore 1/2 Kva = 500va
For a single phase current
500/230=2.174
So the MCB you can put here is a 2.5AMP as it will not be possible to get a exact 2.174amp MCB
Hope this solves your query.
| Is This Answer Correct ? | 6 Yes | 3 No |
Post New Answer View All Answers
Why did lightening arrestor solid copper rod head is sharp on mobile tower top?
How 48-relay (incomplete sequence) functions?
How test for Ddo vector group test condition?
What are the site acceptance tests for power cables, DG Sets, LT panels & 30kVA UPS ?
Name the component u would expect to find in a switchgear assembly?
What is an 86-P or an 86-A trip
1.main parts of generator? what is used A-check,B-check,C- check? 2.what is FM200 system in data centers? 3.difference between pac,ahu?
Why DG set is not installed in Terrace ??
Pl. give me checklist for installation & commissioning of machine tool.
why do we have spikes enough to burn electronic boards, when generators are not grounded
When distance between two pulleys is not fixed, the tension of belt is adjusted by a) driver shaft b) driven shaft c) adjustment screw d) belt
Igfet is a
Define what is the function of anti-pumping in circuit breaker?
what are the interview question asked in wind mill about electrical
What is called limb of a transformer?