If an Instrument has 550 ohm internal resistance and the
cable used for that instrument is 0.5 ohm per meter
resistance. If the voltage is 12volt.How much length cable
can be used? Please tell me its Calculation formula.
Answer Posted / c heman
Assume it is a 4-20 ma tx. 20ma*550= 11volts. minimum
supply is required. so allowable voltage drop is only 1
volt.
so max. 100meter u can use.
got the answer, don,t foget to say thanks.
| Is This Answer Correct ? | 3 Yes | 1 No |
Post New Answer View All Answers
Valve positioner and actuators in detail.
while i check zero check for dp flow transmitter some fluctuating came (0 to 458 kg/h) what is the reason?
Give Detail information about plc,dcs,and scada system?
hi my name is rakesh patel i just complited my be in instrumentation & control now i am going to working as a validation engineer in a poject department so what is a scope in a future as a validation engginer ? what line is good for me can any bady give me complete solution please? your regard rakesh patel
What is the use of each wire in three wire RTD
Define the terms Accuracy, precission, Spam, process tolerance while doing calibration of an instrument? Explaini with an example?
what are the selections available in configuring a burnout protection of a controller? thanks
Q-Explain the different load conditions that will produced different offset which may or may not be acceptable to thhe control function
how to measure draft pressure in transmitter pl. give its single line digram
What is three element drum level control system why its better than single element?
Why is the orifice tab provided?
Sir,I am going to sit for IOCL written test exam. recently.Can anyone tell me the name of 'Objective type Question Book on Instrumentation Engineering ' which will help me. Pl. mail to bidyut_71@rediffmail.com / bidyut.saha2008@indiatimes.com / bidyut.saha09@yahoo.in
Galvanizing.
What is Predictive Maintenance
how do calibrate the valves.. with clear manual