A motor works on 30 killo watts.how much ampers will be
required if it works on 440volts?
Answer Posted / sanjeev
We have to take motor efficiency also ,i.e
I= kw/1.732*415*cos@*efficiency
Then we will get Exact Amp (Nameplate amp)
| Is This Answer Correct ? | 5 Yes | 0 No |
Post New Answer View All Answers
What is transformation ratio what it describes?
how choose conductor&depending upon load
Can I use distributon class/transmission class Lightning arresots for protecting the building? If not why please explain?
WHY SEPARATELY EXCITED MACHINE NEEDS EXCITATION BY DC SUPPLY WHY NOT BY AC
what is alluminium arm in ab conductors
where lt & ht capacitor used
In electrical what is earth(ground)connection, wht is the importance of it, why it is recomended to maitain below 3VAC between Neutral and earthspecially in PLC used machines?
Differentiate between ideal and non-ideal voltage sources?
What is the capacitance values of 132,220,400 & 765 kV current transformer
ANY ONE TELL ME ABOUT generator synchronization panel panel to synchronise 3 gen of 250kva both automatic and manual. 2 gen output vol 415 3ph, 1 gen output vol 400 3ph SEND THE DETAILS DIAGRAM ON THIS EMAIL ADDRESS ayazleo@hotmail.com as soon as possilble best ragrds electrical engineer ayaz mahmood SAUDI TECH
Is MEN and RCD related to each other ?? IF yes then how??
what is the voltages using in movie theaters??? why ??why not other??
difference between semiconductor & conductor & insulator?
how to design coil turns ?
If i have two 3000 kW motors and the whole facility requires a 10 MVA transformer. What would be better installing two 5 MVA transformers(one for 1 motor ) or just a single 10 MVA transformer for both of them. Give reasons for your answer.